Question
Is there a good way to do a master/follower with the VFDs?
Answer
Master/follower is a combination of AC drives and motors to get the follower motor to have a proportional speed of the master motor.
The GS2 and GS3 VFD's have an analog output 0-10 Volt for frequency.
This can be used for outputting an approximate speed control signal.
Error can be from 1% to 5 %, depending on the speed percentage; at lower speeds, the error is bigger.
You may offset the input frequency of the follower using the parameters P4-01 to 4-03
Just connect AO of the master into the analog input for frequency set point on the follower with a wire. Connect the ACM terminals from the master to the follower.
Program the analog output for frequency and the analog input for 0 10 Volt (P4-00 as 2)
If you want higher precision, consider the use of Durapulse drives with encoder feedback.
This will reduce the error to less than 0.5%.
In either case, this is not electronic gearing.
GS4 and GS20 both have 0-10V inputs.
GS20 allows single pulse input feedback which can be set up to command a slave drive which would be the most accurate way to do this
FAQ Subcategory: None
This item was last updated on 2021-02-16
Document ID: 1076
The information provided in the AutomationDirect
knowledge base is provided "as is" without warranty of any
kind. AutomationDirect disclaims all warranties, either
express or implied, including the warranties of
merchantability and fitness for a particular purpose. In no
event shall AutomationDirect or its suppliers be liable
for any damages whatsoever including direct, indirect,
incidental, consequential, loss of business profits or
special damages, even if AutomationDirect or its
suppliers have been advised of the possibility of such
damages. Some states do not allow the exclusion of
limitation of liability for consequential or incidental
damages so the foregoing limitation may not apply.